The special heat transfer coefficient for an impinging jet is a relatively new feature, and we have not gone back to look at the older validation cases involving sprinklers. It may be difficult to assess the effect of the boundary condition for these large-scale warehouse experiments. It might be better to look at a simple test case and do a sensitivity study. |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
|
This is an interesting finding. We have debated whether or not to include a "impingement" heat transfer coefficient. As discussed here and elsewhere, it is difficult within the FDS code to identify an impingement point because FDS only can evaluate a single cell and its neighbors. It does not see "the big picture". There is no single metric for a cell that definitively identifies it as an impingement point. |
Beta Was this translation helpful? Give feedback.
-
|
I'm just catching up on this thread. Just so we are clear, there is an impinging jet HTC model, |
Beta Was this translation helpful? Give feedback.







Uh oh!
There was an error while loading. Please reload this page.
-
Impinging Jet Heat Transfer Model is intended to overcome the not-well resolved velocity area, including below ceiling, above fire. Although this is more significant for heat transfer to the boundaries (e.g. walls), it is also relevant for the sprinklers.
I have looked at the validation experiments but I have not found many examples in which sprinkler is directly located above the fire. However, in specific cases this may be interesting for the sprinkler activation time.
Has this feature been considered as a setting option for sprinkler setups as well? Or was it ignored for sprinkler applications?